Has anyone noticed that the generator does not sync or keeps loosing sync if.
AC low Disconnect is too close to the generator running AC voltage especially during the day with Grid Tie solar connected.
Currently the Generator is running at 227 Volts AC 49hz and seems stable at that setting
Now it seems that If I move the AC low disconnect up to 215 or 220 volts then I find that I seem to be getting no gen sync at startup or Generator sync drop outs when the generator is running. yet the voltages dont show any issues in the VRM
I am wanting to move these as close a I can to the running voltage is 215 or 220 so that I dont get a drop in the AC grid connected solar when the Generator turns off.
NOW if I turn week AC on then I do not seem to get no sync issue, however my charger output drops by 1/3rd so I dont want the week AC on
am using the Assistant PV Inverter support for control the Hz cut off and that works well
I am still investigating this, so if anyone has seen it please advise and add your comments
3 x Multiplus 48/5000 Fw 481 operating in Parrallel 15Kw battery bank is 28Kw Lifep04
CCGX FW 2.65