question

GARY WILLETT avatar image
GARY WILLETT asked

QUATTRO 48V 8kVA Battery Cabling

I am planning for a 48VDC 8kVA Quattro system. Battery cable length is < 2M.

Documentation I've located on the Victron website shows a recommended battery cable size for this inverter of 95 SQMM.

The Quattro has (2) M8 terminals per (+) and (-). I am assuming I can use either (1) 107 SQMM (4/0) per polarity, or (2) 67 SQMM (2/0) same length cables.

Is this correct?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @GARY WILLETT

This is usually explained in the manual for the particular device. This should fit you..

1618115991533.png

These are quite conservative, and at 2m, the 2x 50mm cables should perform admirably.


1618115377103.png (51.7 KiB)
1618115991533.png (37.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tozz avatar image
tozz answered ·

I had 95mm2 cables, but they are hard to handle. They don't fit in the MultiPlus (you can't get the cable lug through the chassis cable opening). So you need to clamp the lug at only one and, and then route the open end through the cable opening, and only then you can clamp the second lug. So if you ever need to do any work on your system you need to cut one of the lugs of. Not ideal.


I used 95mm2 because I figured 'I want to be able to upgrade to a max. of 15 kW, so I thought 15.000W / 48V = ~300A', but I never thought of the fact that I use a busbar and one MultiPlus is limited to 70A DC. So 95mm2 is way overkill for cabling to your MultiPlus. For 70A even 16mm2 would be fine.

I have 4 batteries, 2 in parallel, 2 in series. So I have 2 connections to my busbar. So total charging and inverter power is divided by 2 (2 batteries in parallel). So if I have 3 MultiPlus units, 3x70A = 210A. 210A / 2 = 105A. For 105A 25mm2 would be fine.

So equipping your system with 50mm2 would be plenty. Don't overdo cabling. It's very expensive and the big cables are hard to handle. 95mm2 didn't even fit in my battery (cover wouldn't close anymore)

So what you could do is:

- Use some kind of busbar system. For example, I use a MG Master LV.

- Use 16mm2 or bigger to your MultiPlus units from the busbar. 50mm2 if you want to minimize losses. Don't use 95mm2, it doesn't fit.

- Use 50mm2 to/from your batteries, connecting parallel batteries on a busbar.


6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

What huge lugs do you have?!
We use 95mm² with 12/3000VA Multis without any problems.

0 Likes 0 ·
tozz avatar image tozz Matthias Lange - DE ♦ commented ·

I use SAFAK Elektrik lugs. I don't think they are anything special. they don't unusually large to me.

I might have been mistaken that they don't fit through the chassis cable opening. But I couldn't get the lug on the M8 bolt after routing it through the cable chassis opening. It couldn't make the angle. The battery connection is too close to the chassis, so I couldn't get the cable to bend enough.


0 Likes 0 ·
Show more comments