Hello ,

I have MultiPlus Compact 12/1600/70-16 + Smart Solar MPPT 100/50 all in one.

Im monitoring system on GX display.

Everything is connected and it works good, but i have problem setting state of charge?

Is it possible to have state of charge with this configuration, or i need to install shunt?


image.jpg

T

SOC
image.jpg (4.0 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

You need to activate the battery monitor in the settings of the MultiPlus.
You need a MK3 interface for that or the system have to be online.
https://www.victronenergy.com/live/vrm_portal:remote-veconfigure

1617352048040.png

But the SOC via the MultiPlus is only accurately as long as you have no other DC loads or chargers connected to the battery.
The charging current of the MPPT is counted because of the VE.direct connection to the CCGX.


1617352048040.png (74.5 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kkiksu avatar image kkiksu commented ·

Hi, I have easysolar II GX and we are charging the batteries with solar and with generator via Easysolar II. In this case is generator counted as a "other" charger or is it possible for me to enable SOC and it works correctly? Also why i have maximum charge current value of 35 Amps?


1648200761051.png

0 Likes 0 ·
1648200761051.png (96.3 KiB)
klim8skeptic avatar image klim8skeptic ♦ kkiksu commented ·

Once you start charging your batteries from other than a multiplus, you will need to use a BMV/Smart Shunt.

0 Likes 0 ·
kkiksu avatar image kkiksu klim8skeptic ♦ commented ·

Yes, but the generator is charging via multiplus? not connected straight to the batteries. In this case do i need a shunt? See below. generator is showing at the "grid", not sure why, but don't mind that. ofc if you know how to change it please tell me. :)1648207304404.png

0 Likes 0 ·
1648207304404.png (249.6 KiB)
nevercarry avatar image
nevercarry answered ·

Ok, i will try to set it up online because i dont have MK3 interface.