How do I configure 2 BMVs connected in parallel to a battery bank?

Do I have to double the Shunt Current on the Misc menu or do I have to make it half? Do I have to change the shunt voltage as well?

BMV Battery Monitor
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·

A bit more info please , Why are you wanting 2 BMV units connected in Parallel.


are you connecting two BMV displays to the same shunt or are you installing two complete units inc the shunts


just wondering why thats all - as its highly unusual to parallel shunts

0 Likes 0 ·
Show more comments
2 Answers
Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

Finally, two BMV's can be connected in parallel if the shunt current on the Misc menu is double.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ok now I understand...but like Matthias wrote: best to put them in series...or..

connect two 'shunt pcb's' to one shunt.

0 Likes 0 ·
Vangelis Beligiannis avatar image Vangelis Beligiannis Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Do you mean, using an RJ12 splitter on the shunt and connect to monitors on the splitter? Can I connect a BMV 700 and a BMV 712 on the splitter or must they be identilcal. Of course I will use the shunt of the BMV 712.

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ Vangelis Beligiannis commented ·

No, you can't split the RJ12, that will definitely confuse the ADCs.
Either use two shunts in series or one shunt with two PCBs on it.

0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

If I understand you correctly you have to wire both shunts in series not parallel.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.