Hello, I've been searching and reading through various threads trying to find information on this topic but am only finding bits and pieces. I'm trying figure out two things
- Is there some kind of chart somewhere that gives rough approximation of the inverter wattage over the continuous rating (2400 @25c), and how long that wattage is available? I see the 6000 watts peak, but assume there must be some kind of algorithm for the amount of wattage over continuous available for a certain duration (ie @25c 3000 for 8 mins, 3600 for 6 mins, 4200 for 4 mins, etc.)
- In terms of sizing the AC-OUT-1, for the main circuit breaker I see the manual shows 50+13 amps if using Power Assist, but assuming I'm not going to use power assist can I just use a 50 amp main breaker for my AC distribution panel? Of course assuming I'll use the correct size wire for the load.
Thanks