question

llubi avatar image
llubi asked

Multiplus ("plastic" exterior) low amperage charging

Hi All!

My system is in a campervan, and it's:

1 x lifepo4 280Ah 12V

1 x Multiplus 12/1600/70

1 x BMW712, CerboGX, OrionSmart and MPPT 100/20

Wiring from battery to bus are 70mm2, wiring from multi to bus are as big as it fits, 50mm2. About 1,2m each cable.

Multi has been configured with Ve.config to lifepo battery, 52A max charging, and I think nothing more to comment.

Cerbo has DVCC engaged, with the option of limit charging disconnected.

2-3 times, I connected the van to shore, with the battery at around 50-60%, and the multi all the times make the same, start charging at +-50A, and 2-3 minutes later, go down to 30A and finishes charging at 15A. Battery stills at 50%, and temperature of the battery from 10 to 18 degrees Celsius.

What am I missing?

Thanks!

MultiPlus Quattro Inverter Chargercerbo gxmultiplus ve.bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@llubi

If this is a new install then you need to give it a bit of time and a cycle or two, to correctly calculate the SOC.

The BMV calibration maybe out.

https://www.victronenergy.com/blog/2017/04/13/instructional-video-how-to-optimise-the-bmv-700-series-sync-parameters/

https://www.youtube.com/watch?v=yMJ_vzB2avE

Of course your batteries will also have a BMS inside and they will be limiting the charge to the cells because it is doing its job.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

llubi avatar image llubi commented ·

It’s not a BMV problem, is the multiplus not charging using the configuration. Also not a new install, just the Multi is new.

I didn’t said before, but battery has no BMS, I configured 2 x battery protects to ensure battery won’t have problems

0 Likes 0 ·
seb71 avatar image
seb71 answered ·

What voltage does the battery reach when charging is finished?

17 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

llubi avatar image llubi commented ·

14.20 to Absorption, 13.50 to float. But this is happening under 13 volts

0 Likes 0 ·
seb71 avatar image seb71 llubi commented ·

Your battery has a BMS?


Edit
I saw your other reply. So no BMS.


Did you measured each cell voltage?

0 Likes 0 ·
Show more comments
jwfrary avatar image
jwfrary answered ·

Have you checked the lithium battery option in ve.configure?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

llubi avatar image llubi commented ·

Yes. First by the new on-line VRM option. As It didn’t worked, bought the MK3 USB cable and made it again. No changes, if I reset the Multiplus it charges at “full” speed for 2-3 minutes, then it goes to 15A, reset and works again

0 Likes 0 ·