question

Alexis Kalogerakis avatar image
Alexis Kalogerakis asked

AC-input for 3phase Multiplus system

Can a 3phase multiplus system accept as Input a 3phase generator without neutral (only L1, L2, L3) (Delta).

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

Hello, No, as the units are essential 230Vac (or 120Vac depending on the area) the input needs to match this. When the input is 3p without a N there is no correct voltage reference per unit so it will not be accepted.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexis Kalogerakis avatar image Alexis Kalogerakis commented ·

Thank you very much for your answer, that was what we expected.

0 Likes 0 ·