Victron Charge Controller SmartSolar 250/100 has no LED

We have 4 units of SmartSolar Charge Controller.

CC1 does not have LED Status display and system charging got slower

CC2 has an error 38.
CC3 & CC4 has no issues

161378820-923480405236562-4177019637744935793-n.jpg161319634-1865093586977962-8984529522506317620-n.jpg

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Can you connect to #1 via VictronConnect?

Did you try this for #2?:
https://www.victronenergy.com/live/mppt-error-codes#err_38_err_39_-_pv_input_shutdown

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harry-chavez avatar image harry-chavez commented ·

160202737-265897505029567-7370038346388822186-n.jpgCC#1 is not shown on the VictronConnect only CC#2,3&,4


0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ harry-chavez commented ·

Check the voltage at the battery and PV terminals of #1.
If the voltages are ok try a power cycle -> disconnect PV first -> disconnect battery -> wait a few minutes -> connect battery (the MPPT should turn on now) -> connect PV.

If #1 still won't turn on it seems to be defective and needs to be replaced -> contact your dealer.

0 Likes 0 ·
harry-chavez avatar image harry-chavez Matthias Lange - DE ♦ commented ·

Batt Voltage is 53.1 and the PV when not connected to MPPT is 167 V. When I turned on the DC Breaker of PV the voltage at the terminals of PV input in the MPPT is only 53.1 same as the Batt Voltage.

I already did that power cycle procedure. The MPPT's LED do not lit on and I can't detect it using Victron Connect.

The MPPTs might be defective. What could have caused this issue?

0 Likes 0 ·
harry-chavez avatar image
harry-chavez answered ·

@Matthias Lange - DE

Sir now all charge controllers are not functioning.

What should we do?

CCGX is our current GX device. We would replace it with CERBOGX and detach the PV supply and battery connection cables to restart the charge controller? Please advise if this will resolve the issue.

Thank you

1621766426186.png


1621766426186.png (660.3 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

@harry-chavez

I notice a Tigo label in your pic. Are you running those on the panels?

0 Likes 0 ·
harry-chavez avatar image harry-chavez JohnC ♦ commented ·

Yes sir.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ harry-chavez commented ·

Tigo optimizers dont mix well with mppt's.

0 Likes 0 ·
harry-chavez avatar image harry-chavez klim8skeptic ♦ commented ·

The Tigo that we used is and RSD TS4-A-2F.

Should we remove the Tigo Units? Or should we try to remove the battery and PV Connection from the MPPT for it to restart?

0 Likes 0 ·
Show more comments
JohnC avatar image
JohnC answered ·

Hi @harry-chavez

Re the Tigo's.. From the Bluesolar mppt manual..

9.5.8. Optimisers cannot be used

Do not use solar panels with optimisers together with the solar charger.

Nearly all optimisers contain an MPPT or other tracking mechanisms and this interferes with the MPPT algorithm in the solar charger.