I have a Quattro 10k setup for 60hz/240 on my boat. AC1 - wired to Gen set at 42a max. AC2 - Shore Power @ 50a default, but change to 30a for some locations i plug into.
The Quattro properly will leverage the full amperage available from AC2 for either pass through, charger, and will also go into assist mode when my draw is larger than I indicate when on AC2 (shore) mode. So, all is good with AC2.
However, when i run my Gen, with 42a set for the load limit (10kw gen), i get strange results.
if the draw on the Quattro is roughly 4000-4500 watts (varies a little) or LESS, the Quattro will supply the voltage through the inverter, AND supply the remaining 4000-5000 watts to charging as needed. (as it should)
However, if i put a larger load on the house.. say 5000 watts, the Quattro goes into Invert Mode and stops all charging. this is very consistent and repeatable.
the Quattro knows it can support up to 10000 watts as if the house draw is under roughly 4k-4.5k it will pass through and charge drawing up into the 9000 watt range properly.
Why the heck is it doing this? I have read everything i can find and have tried using the Dynamic Current Limiter, and Power Assist with 2.0 Boost Factor
What would make AC1 and AC2 behave differently? this is beginning to be a huge issue as the only way around it is to shut a lot of stuff off to get the draw down, which then will eventually cause the charger to kick back in...