Connecting 280W of panels to BlueSolar 75/15

I have a BlueSolar MPPT 75/15.

On the roof, I already have two photovoltaic panels (Kyocera KD140GH-2PU) of 12v, 140W each. They are connected in parallel. In their specs:


At 1000 W/ m² (STC)*

Maximum Power [W] 140

Maximum System Voltage [V] 1000

Maximum Power Voltage [V] 17.7

Maximum Power Current [A] 7.91

Open Circuit Voltage (VOC) [V] 22.1

Short Circuit Current (ISC) [A] 8.68

Efficiency [%] 13.9

At 800 W/ m² (NO CT)**

Maximum Power [W] 101

Maximum Power Voltage [V] 16.0

Maximum Power Current [A] 6.33

Open Circuit Voltage (VOC) [V] 20.2

Short Circuit Current (ISC) [A] 7.03

NOCT [°C] 45


Can I directly connect these panels as they are to this charge controller?

Solar Panelmppt charging
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glenn748 avatar image glenn748 commented ·

The battery can be kept from over release by interfacing all heaps to the charging outlet.


UPSers

0 Likes 0 ·
4 Answers
seb71 avatar image
seb71 answered ·

They have different voltages. So not a good idea to connect them in parallel.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m1ck avatar image m1ck commented ·

They have exactly the same voltage, as they both are the same maker and model. They have been working for years in parallel with an older PWM charge controller. Are you comparing 'at 1000 W/m2' versus 'at 800 W/m2' values?

0 Likes 0 ·
seb71 avatar image seb71 m1ck commented ·

Yeah, I thought you have two different panels.

0 Likes 0 ·
seb71 avatar image seb71 m1ck commented ·

You will never get 280W into the battery (that charger has a 15A current limit into the battery), but in cloudy days an oversized PV array will help.

0 Likes 0 ·
Show more comments
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @M1CK,

yes you can connect them to the MPPT controller. They are a little low on maximum power voltage. Be aware that the MPPT to start charging requires a voltage of at least 5V above battery voltage. But when you connect them in series, it should be no problem.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offtaps avatar image
offtaps answered ·

You should not connect them in parallel as Isc of such an array is greater than the maxi allowed for the 75/15 (15A)

Just connect them in series.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

spanner avatar image
spanner answered ·

The perfect world calculation is (140w x 2) = 280w / voltage (12v) = 23 Amps - in reality you wont get that output of 280w as the spec you provided is 6.33A. As above the VOC of your panels is 20.2 x 2 - the mppt will go up to 75v. So conclusion is YES ;-)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

For Standard Test Conditions:

Isc = 8.68 A

Voc = 22.1 V

0 Likes 0 ·