Multigrid 48/3000 inverter priority ?

I have to change my current setup from ESS "feed in excess power" to "island mode / inverter priority" as feed-in is no longer tolerated by grid supplier.

As far as I understood the deprecated "self consumption hub 2" with "prevent feedback to grid" is the only way to control the power of non Fronius PV inverters, connected to ACout, by shifting frequency. ESS does support Fronius only - correct? My Inverter (3,5kWp) doesn't allow true power regulation, but as a workaround I can at least switch it off, by setting the upper frequency limit.

I understand this is not the best setup but I need a solution asap.

I plan to connect the loads to ACout1. Average load is 0.5kW, usually not exceeding 3kW.
In case load increases to maybe 4.5kW I hope the "Grid Assist", properly set, will handle it.
Battery is LG Chem 6.5

In case the Inverter fails I'd like to have th eoption to manually switch my L1 loads to the grid

Please let me know your thoughts

Thanks

I skip all the fuses and wiring details, just the principle

1614707889719.png

Phoenix Invertermultigrid
1614707889719.png (135.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
vicky avatar image
vicky answered ·

its me again...
Before changing anything, I updated my VEconfigure and theESS assistant and played a bit.
If my interpretation is right, the ESS assistant does also allow to reduce PV inverters power if connected to AC out.
Can somebody please check & confirm ?

Txs a lot


1614785872611.png

1614785911371.png


1614785872611.png (47.0 KiB)
1614785911371.png (12.6 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

vicky avatar image
vicky answered ·

I am stuck, obviously missing the point :o(.

Reconfigured my ESS to a Self consumption HUB assistant 2 v3 where I did not change any wiring.
Used VE Configure, did the settings and sent them to the Multigrid - saved successfully.


As SoC is sufficient I expected the Multi to start the inverter feeding the "critical loads" on ACout1.

Unfortunately after restarting the Multi it stays off. Mains and LowBat LEDs are blinking.
Active AC Input disconnected.
I guess it is an obvious point I am missing, but which one?

1615829393900.png1615828970812.png



1615828970812.png (77.3 KiB)
1615829393900.png (18.9 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Phoenix Inverter product page

Phoenix Inverter Smart product page

Additional resources still need to be added for this topic