The system is configured with two 10K Quattros 120V/240V Split phase with 4 SmartSolar Charge controllers, a Lithium Battery with a CAN-bus BMS and it also has a Lynx Ion Shunt. ESS is configured in the Venus GX
I would like the GenSet to turn on when the Grid is not available and the Battery are discharged to 50V DC and provide power to the loads and charge the battery. The Venus relay are able to turn on and off the GenSet with no problem. When the condition are met for the Venus to command the GenSet, it turn on. After a few minutes an alarm is received in the Venus stating "Generator not detected at AC-input" and in fact the GenSet is on and power can be manually measured at the input of the Quattros, but the Quattros continue to discharge the battery.
1. I wanted to know if there was a difference between attaching the Grid to AC IN1 vs AC IN2 and the same question for the 30Kw Diesel Electrical Generator that provided 120V/240V Split Phase.
2. In the VE Configure app AC1 is labeled as (priority) and AC2 is not. What does "priority" mean?
3. In the VE Configure app there is an "Overrule by remote" that can be changed in either AC IN1 and/or AC IN2. Why would I want these checked?
4. In the VE Configuration app the Grid code is set to "Other" and both LOM are set to Type B. Should the GenSet (AC IN2) be set to disable?
5, Having the UPs function on, could this be the cause of my problem?
Would appreciate any help with this configuration.