BMV-712 with Lynx Distributor

is there a way to power the fuse lights on the Lynx Distributor via the BMV -712 Shunt. can a splitter be used on the RJ 12 port on the shut to have on leg go via the RJ 12 cable to the BMV-712's battery monitor and the other leg via the RJ11 cable to the Lynx Distributor?

BMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Mark avatar image
Mark answered ·

the rj10 cable in the distributor requires a 5V supply for the LED’s to function

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thomb avatar image
thomb answered ·

on the UTP port on the BMV-712 shunt, can i get this 5 V supply to the Lynx Distributor

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @ThomB

No, this cable has nothing to do with the Lynx rj10 cable, don't connect it to anything else than the BMV itself.

0 Likes 0 ·
Mark avatar image
Mark answered ·

You can power up the unit by providing a 5VDC power supply to the correct pins of the 4P4C connector/lead - 5VDC to Pin #1 and ground/negative to Pin #4.1614330817756.png

In case you have a VenusGX, this conveniently has 5VDC output terminals that you can use. If you have a different Venus device, such as a CerboGX or a CCGX, you could make up an adapter cable to take 5VDC from a spare USB port.

Alternatively, you can purchase a small 12V/24V/48VDC to 5VDC DC-DC converter.

As already pointed out by others, do not attempt to connect the Lynx Distributor cable to the to the BMV cable somehow.


1614330817756.png (46.3 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark commented ·

The plugs/leads for the Lynx distributors are rj10

0 Likes 0 ·
Mark avatar image Mark ♦♦ Mark commented ·

Yes sorry, you are correct that it's not an RJ11 connector; I have corrected my answer.

But I quickly googled and technically 4P4C or 4P2C connectors (originally used for telephone handsets) do not have an official ACTA Registered Jack (RJ) designation, since they do not interface with public networks. Unofficially 4P4C and 4P2C connectors have been referred to as RJ9, RJ10 and RJ22.