Hello,
Recently got a system consisting of:
1x Quattro 48/3000/35
2x Pylontech US3000c
2x BlueSolar Charger MPPT 150/35
1x CerboGX
As part of my testing I ran a load until shutdown. What happened is that the whole system turned off at the low voltage point. The Pylontech shows the RED alarm LED. The Victron setup does not seem to see any DC power at all at that time (touch display off etc).
It would be nicer if there is a shutdown mode where the inverter is disabled (but still powered, just not generating AC). That way the display still shows what is happening. At some point the batteries are going to turn off completely and then whole system will be down.
I've had bad experience (with another vendor) where it becomes a real struggle to get the inverter/charger to wake up when there is (generator) AC, but not DC yet.
Is that not an issue with the Victron, as soon as I apply AC the system comes back to live?
Also, when the system was in shutdown, non of the console commands on the Pylontech seemed to indicate a powered down state :) I must be looking at the wrong command since the inverter saw low voltage over CANbus. What is the correct command to see historic shutdown reasons?
Bas