question

benji avatar image
benji asked

VE.Bus BMS #7

I have a problem installing a Ve.Bus BMS. When I connect the VE.Bus BMS to my 24/3000, the error message "# 7 Ve.Bus BMS without assistant" is displayed on the ColourControl. In addition, the "inverter on" indicator flashes on 24/3000. How can I fix this?

BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

You need to setup your 24/3000 inverter correctly . you need a MK2 or MK3 and then the config software from victron and then setup and install the correct lithium assistant. to suit your Cell balancing units

presuming this is what you are using the VE BMS for

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

benji avatar image benji commented ·


is a direct connection of the 24/3000 to the pc also possible?

0 Likes 0 ·
boekel avatar image boekel ♦ benji commented ·

You need a cable...or...as you say you have a colour control: If the CCGX is connected to internet, you can use remote configure.

in the VRM portal, go to 'device list' and choose 'Remote VEconfigure'

you'll need the VEconfigure software.

0 Likes 0 ·
benji avatar image benji boekel ♦ commented ·

I have done that now. what do I have to change exactly? under "General" only the three values of the battery or something else?

0 Likes 0 ·