question

mike-b avatar image
mike-b asked

BMV712 connection for midpoint voltage

I have 6 Firefly L15 (4V) batteries. I would like to wire these in series(3x4V) /parallel to have 12V/ 900Ah. I am installing a BMV712, and would like to have Midpoint voltage monitoring. Please show a diagram of how to wire this configuration. The "Quick Start" guide does not show a diagram which seems to match.

Thank you

BMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Mark avatar image
Mark answered ·

Hi Mike,

Sorry but with those particular batteries in a 12v setup you physically can't access the midpoint (6v), so midpoint monitoring is not posible The voltage at the link terminals/cables would be 4v & 8v.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

vineyardgray avatar image
vineyardgray answered ·

Each Firefly 4v battery are actually two 2v cells externally connected with a series busbar. It should be possible to get to the 6v midpoint.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mike-b avatar image
mike-b answered ·

OK, 2 opposite answers, can we get some further clarification from Victron?

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

The answer has nothing to do with Victron - Victron do not make the batteries being discussed.

But this is not a complex matter...

If the link between the 2 cells can somehow be physically accessed to attach a wire for the mid point monitor (ie. if they are external), then yes it will work. But if you can't then it won't...

Basically all batteries are internally made up of separate 2v cells, but you typically can't access the links

0 Likes 0 ·
Show more comments