Hi,
In a system with a Multi 2, SmartSolar MPPT and a 2-wire BMS will the MPPT stop charging as well when Multi is asked to stop and the same goes for charging on low battery signal from BMS ?
/peter
Yes, EES reason code #3 will show - "BMS has disabled charging". VE.Bus BMS menu will show "Allow to charge = No"
MPPT's will support loads, but charging current to the battery will not be allowed.
@WKirby Great thx, now another question arrises. How can the MPPT support loads if it's not charging i mean doesn't it provide power on the battery positive/negative which also goes to battery ?
There are actually two options when setting up the 2-wire BMS Assistant:
Force to float Voltage or Disable charger.
I use force to float, this way the MPPT charger only makes the power needed to power the loads. The only battery current is enough to maintain the float Voltage (not very much).
Indeed the battery is loaded to FORCE to the float Voltage as quickly as possible, MPPT power will be reduced or cut until the float Voltage is reached.
In my case, full power grid backfeed takes place to reach down to float Voltage very quickly.
I did not use "Disable charger" option.