Multiplus 12/3000/120-50 will not turn on

I have a new multiplus connected to a 400ah battery bank through the Lynx distributer. Also have 120v shore power to ACin. I read 13.4v on the DC in side at the multiplus terminals and 110v on the AC side. Nothing happens when I hit the on button - either for inverter or charger. DC side is 4/0 cables with 400 amp fuse. AC is 10AWG through a 50 amp fuse/breaker. Not an engineer. Thanks.

MultiPlus Quattro Inverter Charger
11 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offroadflow avatar image offroadflow commented ·

Did you check the voltages directly on the connectors of the inverter?

0 Likes 0 ·
nbbw avatar image nbbw commented ·

I did measure the voltages directly on their terminals of the inverter.

0 Likes 0 ·
Paul B avatar image Paul B commented ·

have you got anything else plugged into the VEbus ports.

or try

have you got a MK3 unit if so connect this to your computer and open the victron ve configure app and see if it turns on. if it does then just remove the MK3 and you are now going.

the above is just a sugestion

0 Likes 0 ·
nbbw avatar image nbbw Paul B commented ·

All I have connected is the remote start (Digital Multi control GX) into its RJ45 port. It also does not turn the unit on. I don't have the MK3 unit. I was hoping it would work out of the box as advertised and I would not have to hack it. Thought maybe I just was missing a hidden "go" switch or something. Ive reached out to Victron distributor but haven't heard anything.

0 Likes 0 ·
offroadflow avatar image offroadflow commented ·

Maybe the remote on/off connection inside the inverter is missing..?

0 Likes 0 ·
nbbw avatar image nbbw offroadflow commented ·

No the switch is there - I'm plugged into it plus, I am pretty sure it should turn on without the remote switch attached. I have tried it with the remote switched plugged in and not plugged in.

0 Likes 0 ·
offroadflow avatar image offroadflow nbbw commented ·

I'm referring to the tiny cable connection inside the inverter...

0 Likes 0 ·
nbbw avatar image nbbw offroadflow commented ·

screen-shot-2021-02-09-at-71107-am.png



The blue circle labeled "B" is the RJ45 connection for the GX remote switch, which is present. The small square above it labeled "H" is the jumper switch if you wanted to connect your own three way switch. Right now the jumper is set as it cam from the factory with the cables connected for "on" operation. I have tried switching the "H" jumper cables around with all possible iterations but still no luck. Are either of these the tiny cable connection you are referring to? Thanks by the way for the help.

0 Likes 0 ·
offroadflow avatar image offroadflow nbbw commented ·

Yes, I referred to H.

Sorry then...

0 Likes 0 ·
nbbw avatar image nbbw offroadflow commented ·

Hey no problem! I really, really appreciate the help.

0 Likes 0 ·
offroadflow avatar image offroadflow nbbw commented ·

No prob.

Best to hook up a computer to see if you can at least access the inverter this way and check all the settings...

0 Likes 0 ·
1 Answer
JONI RAVAI avatar image
JONI RAVAI answered ·

Hi Guys. I'm having the same issue with a 12/3000 Multiples. I've had the MK3 connected with all the remote jumper connected but was not able to see the inverter on the Victron Connect App. What could have been the issue?

Looking forward to the assistance.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offroadflow avatar image offroadflow commented ·
"...the app"?

I assume you mean the computer program, NOT the mobile phone app..?

0 Likes 0 ·