Over powering smart solar controller

Ive got a smartsolar 100/20 yet to be installed. This is going into my caravan and am loking to get 2 house panels to mount flat on roof. Using the victron excel spreadsheet when i input 2 x190w panels in series or parallel it comes up warning of over 30% overpowered. Originally was looking for 2 x170w panels in series but 190s seem easier to get. Would using 180s be a problem?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
seb71 avatar image
seb71 answered ·

Look at VOC for the panel.

String VOC must be under 100V for that charger. Leave some safety margin for cold temperatures, when the voltage can be higher.


Also, usually 60 cell panels have best prices per Watt.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

haudidier avatar image
haudidier answered ·

your smartsolar 100/20 is limited in solar voltage. Its maximum input voltage is 100V DC.
So if you put two panels in series, you have to check that 2xVoc < 100V (Voc is the open circuit voltage of your panel, see the datasheet of your panel).

And as seb71 says, "Leave some safety margin for cold temperatures" because when the temperature decreases, the solar voltage increases.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-p avatar image paul-p commented ·

These panela are 44.5v voc. Coldest temp here would be 4 degrees Celsius

0 Likes 0 ·