I'm connecting Multiplus 24/800/16 -16 inverter to four 12V 200Ah battery. What is the appropriate fuse/circuit breaker size to fix in between the inverter and the battery bank?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
I'm connecting Multiplus 24/800/16 -16 inverter to four 12V 200Ah battery. What is the appropriate fuse/circuit breaker size to fix in between the inverter and the battery bank?
the max or peak power output on this inverter ia 1600w so at 24 volts this is around 66 amps
so a fuse size of say 70 amps should be fine lower is ok as well, but if it peaks on a high load the fuse may blow.
I presume that the wiring size is capable of taking that 70 amps as well.