I'm trying to get the water tank level sensors connected to the Venus GX. But how.... I can't really get any information out.
I have activated the analog tank sensor on the Venus GX.
The level sensor has two connectors and ground. See picture.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I'm trying to get the water tank level sensors connected to the Venus GX. But how.... I can't really get any information out.
I have activated the analog tank sensor on the Venus GX.
The level sensor has two connectors and ground. See picture.
On the bottom right picture of that document it shows only two connections (on of which seems to be ground).
I would think you should use the G and ⏚to go to the Venus GX.
Did you choose European 0 - 180 Ω ?
Do you have a multimeter to check at the terminals of the sender?
You should be able to measure between 0 -180Ω depending upon the position of the float.
Start at the sender end and then fault find back, you should have similar resistance range at the Venus end of the cable. Once we know that the sender is presenting a resistance to the Venus, we can work from there.