question

rsnt avatar image
rsnt asked

MultiPlus 48/3000/35 output current cleanliness?

I'm unable to find any detailed information on the output power of the MultiPlus with regards to its cleanliness and sine wave stability. What kind of sine wave does it output, and is this unit suitable for electrical equipment such as speakers for instance. Any info would be appreciated.

Venus OS
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@RSNT

It is s true sine wave inverter, tried it on an oscilloscope at work. Even under load it is stable.

My husband is a bit of a sound enthusiast, has built his own amplifiers with studio monitors from a recording studio. Best sound from he amps built is when we disconnect from grid power and let the Victron determine the power quality.

There is no hum or other whining sound heard (if there are no issues with the amps or cables themselves).

0 Likes 0 ·
Show more comments
1 Answer
wkirby avatar image
wkirby answered ·

This is the output of my MultiPlus 24/3000/70 with a 2KW load:


1611938135600.png


1611938135600.png (340.3 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rsnt avatar image rsnt commented ·

Thanks for this osc plot here. Really clean looking sine wave here. Would you say these inverters will be good then for computer equipment?