Have been having problems on this site with premature load shutdowns
2 x Quattro 24/5000 in Parrallel
1 x CCGX and VRM connected
it was on 476 Firmware we moved it up to 478 due to possible fixes to abnormal shut downs with ripple involved.
Now with 478 and nothing else changed we get expected devices error, But ONLY when we turn the inverter OFF using the CCGX (2.60fw) then the error appears, turn it back on via the CCGX and the error goes away.
Still having HIGH load shutdowns with impedance devices (ie AirCon Chillers) when we are only at around 50% load.
(Note we are aware that Ripple is high around 1v we are working on reducing that this coming week)
(It was NOT doing this on a earlier FW (did not record the version) we went to 476 because one main board had to be replaced)
Advise if VRM/remote access is needed.