Hi Folks,
I'm looking for advice on the configuration of a Victron EasySolar 3KVA system configured as grid-connected, zero-feed in ESS. I have eight 12v 100AH Hankook DC31MF leisure batteries configured as 4P2S giving me a 48v 200AH bank. The battery SOC seems sit around 95%, occasionally hitting 100% in the summer.
This has been running for a couple of years but I'm finding that most of the time the system seems to be cycling between a few minutes of Inverter On (discharging) until I see a "Low Battery" warning, followed by a few minutes of charging. The other "issue" I have is that whenever the mains power fails there seems to be insufficient battery power available to power the system - this results in an outage.
So, I have a couple of questions:
1. Is the battery capacity "sufficient" to use in this configuration and should it be able to perform as a UPS (albeit in a limited capacity) when mains power fails?
2. Is the discharge/charge cycling to be expected - looking at the system now I have 120W AC load and its cycling every few minutes...?
3. In the absence of any specific data for these batteries, I have them configured as Gel/AGM as this seems to match the only data I manged to get from the manufacturer:
Manufacturers Recommended Battery Voltages
Daily Cycle: 14.4 (57.6)
Float: 13.2 (52.8)
EQ: 15.5 (62)
My Configuration (Note: Float is a little higher than manufacturer recommended):
Dynamic Cutoff is also at the default for Gel/AGM - is this ok?
Restart Offset:again default for Gel/AGM is this ok?
Any help/advice gratefully accepted!!