question

Mathew Hamilton Green avatar image
Mathew Hamilton Green asked

How efficient is my Victron 12/500 inverter?

Does anyone have a link to a graph or something? :-)
Thanks!

MPPT ControllersPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Alexandra avatar image
Alexandra answered ·

@Mathew Hamilton Green

I have found it depends on your load and set up. So it is a difficult one to answer in a datasheet as there are so many variables. Even percentage load of inverter capacity is a factor.

The best way to know how efficient your personal setup is, is to run a known load on your system, and measure how much is being drawn from your battery and work out the percentage from there.

For example

I have a 24/3000 and am running my heating element of 1500W yest i am drawing 1600 watts from the battery I know I have about a 93% efficiency for that circuit and load. Of course I have a low frequency Multiplus inverter not a high frequency like the newer ones, this is also a factor to consider. Recently increased the battery cable size from 50mm to 95mm ad made the system more efficient that way.

I have used a simple element as an example of a load as it has a good power factor. Some led bulbs have a power factor of 0.5 so a 4w bulb can actually draw 8w from a system. So checking with a clamp meter on incoming and outgoing is helpful to see what side the inefficiency is.

16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Alexandra

Hi,

Are those numbers for real, or just mathematical an example?

My MP-II 48/3000 paints quite different picture.

Same type load (heating element) but efficiency is much lower.

Very disappointing 84.4%. :(

Regards,

Marek


inv-eff.jpg

0 Likes 0 ·
inv-eff.jpg (71.9 KiB)
Alexandra avatar image Alexandra ♦ marekp commented ·

W

@MarekP

No we used the color control as well. But checked numbers with a clamp meter.

Found interesting changes when

  1. Battery type was changed is from lithium to agm. Battery efficiency is a factor.
  2. Cable size changes as well we use 95mm now (makes sense as there will be less resistance). And the usual removal of extra things in the wiring and left just fusing and the bmv shunt. Good lug crimping also makes a difference. All resistance connections are important.
  3. The other thing that made a difference was measuring with the bmv shunt as the multi itself has no way to actually measure power from the battery. So the figure coming out is usually an assumed amount.
  4. Wiring on the ac output was also 'tuned up'

Thats why we say efficiency to some degree can be affected by setup.

We have a 24/3000 which is technically less efficient conversion wise.

0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

I understand all your points but, as you can see in my picture, the numbers are from MP-II unit itself.

It calculates incoming/outgoing power from battery/AC by measuring the current and voltage on its battery and AC terminals.

Cables, fuses shunts are out of this equation.


Regards,

Marek

0 Likes 0 ·
Show more comments
Alexandra avatar image
Alexandra answered ·

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mathew Hamilton Green avatar image
Mathew Hamilton Green answered ·

Nice thanks! :-)

I have two 120Ah batteries in parallel and my Mac Mini M1 and monitor is drawing around 4Amps, when in use and my LED smart light around half an amp... I am trying to see how long I can go between charges because in theory I should get around 24 hours of operation. I also wanted to check the batteries as I have had them just over a year and wanted to see how they were doing! :-)

Just wanted to check everything.

I'm about to install another 270W solar panel to bring my total to 810W as I am determined to be able to power all my needs from the sun even in the winter in England. Today I was drawing around 3Ah all day... I am in a motorhome not in situ somewhere! :-)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Mathew Hamilton Green

Hi,

If I understand your question correctly, you have 2x12v batteries 120Ah each.

That gives you 2880Wh of energy when they are fully charged.

If they are of Pb type, you can only use half of it if you want them to last the reasonable time.

Your load is 4A at 230V that makes it 920W per hour

If we assume that your inverter has 100% efficiency and 50% use of battery, you have around 1h and 33 minutes of battery power when there is no Sun to charge your battery.

Regards,

Marek

0 Likes 0 ·
ripper avatar image
ripper answered ·

https://www.photovoltaikforum.com/thread/133886-effizienzkurven-wechselrichter-victron-oder-fahre-ich-mit-2-wechselrichtern-wirk/


Here is a Graph of a 375 vs an old 3000 I measured. It is always a curve. Sweet spot is around half of nominal load which will be similar on your 500 unit. I am running 2 Inverters, above 200ish W load the little 375 uses more battery power than the big 3000 inverter. If you are off grid no load consumption is the more interesting value. 4W or 0.5W (eco mode) for the little one vs 12W for the 3000 vs 25W cheap chinese product 24/7

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.