Multiplus 2, load the Battery function not needed

Hello everyone,

we are using a Multiplus 2. In our case it should only invert the power from the battery and take power from the grid, if necessary. It is main task is not to load the Battery! In order to load the battery, we use a PV. I could not find anything about turning off the Load function. Please help

Multiplus-IImultiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Just disable the charger:
1610351025046.png

OR use the ESS-Assistant:
https://www.victronenergy.com/media/pg/6292-ESS_design_and_installation_manual-html5/index.html?lang=en

BTW "load" means discharge, what you mean is "charge" :)


1610351025046.png (51.5 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Cansin Sari avatar image Cansin Sari commented ·

Hey thanks a lot Matthias. Just one more question: we want to connect 2 pylontech 2,4KWH to the inverter, should we place a DC Breaker between the inverter and Battery?

Manual lists those protections for the inverter

a. Ausgangskurzschluss

b. Überlast

c. Batteriespannung zu hoch

d. Batteriespannung zu niedrig

e. Temperatur zu hoch

f. 230 VAC am Wechselrichterausgang

g. Brummspannung am Eingang zu hoch

Greetings from Berlin