Smart Solar 100/30 over voltage every day

I have a MP100/30 charger. It's set up to charge a LifePO4 battery and despite my charge profile settings (absorption 14.2, float 13.5, absorption duration fixed at zero minutes), I'm seeing 15 volts plus in the history screen every day. Even when the trailer is sitting in the rain on an overcast day. The only thing running is a small 130l compressor fridge. Worried about damaging my 200ah new battery. Any ideas would be appreciated. Images of the settings and history below. Cheers. Stephan

img-4286.pngimg-4287.png

MPPT Controllersbattery chargingMPPT SmartSolarovervoltage
img-4286.png (214.8 KiB)
img-4287.png (202.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
seb71 avatar image
seb71 answered ·

Is the temperature compensation disabled?

That setting is missing from your screenshots.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stephanv9 avatar image stephanv9 commented ·

Hi @seb71 , Temp compensation is disabled. Cheers. Stephan

0 Likes 0 ·
JohnC avatar image
JohnC answered ·

Hi @Stephanv9

It may be just 'spikes', possibly caused when your fridge switches in or out.

Try setting up the Trends graph with battery V and Current. That may indicate something that you can relate to the cause of a spike above the set V level.

The mppt can overshoot, but shouldn't worry your battery.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stephanv9 avatar image stephanv9 commented ·

Hi @JohnC, Thanks for the quick reply. I tried setting up the trend for a while this morning. Interestingly, the voltage seems to jump up to 15 or sometimes even 16.28 volts for a second or two every once in a while. I just caught it three times in the space of 5 minutes. The fridge cutting in and out doesn't seem to have any bearing on it. It happened a bit before the status changed to float. There's nothing else in our camper other than some LED lights, which were not on. I'm a bit confused over it to be honest.

I see some other suggestions that recommend turning the absorption voltage down to 13.95 instead of 14.2, but I think that was to counteract "spikes" when load goes on and off when the battery is fully charged. Do you have any other suggestions? Cheers Stephan

image-123986672.jpg

0 Likes 0 ·
image-123986672.jpg (155.9 KiB)
Show more comments
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

What battery do you have exactly?

Maybe the BMS is cutting off the charge current due to a high cell voltage. In that moment the output voltage of the MPPT can rise for a few seconds.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stephanv9 avatar image stephanv9 commented ·

Hi @Matthias Lange - DE I am using a lithium valley Chinese 200ah battery. https://www.lithiumvalley.com/battery/12v-200ah-lifepo4-battery/. Over charge voltage is 14.65 so with my controller set at 14.2 it would be unlikely to be the problem. . Keen to know any other thoughts on this. Cheers Stephan

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ stephanv9 commented ·

14.65V for the whole battery but the BMS should also cut off charge if only one cell gets to high.

Do the battery have some kind of smartphone app or interface to check the cell voltages?

0 Likes 0 ·