question

lemonjelly avatar image
lemonjelly asked

BMV SoC and Battery Cell status not alligning?

2 x 150ah Victron SmartLithium batteries:

Battery 1

  • Cell 1: 3.05V
  • Cell 2: 3.04V
  • Cell 3: 3.05V
  • Cell 4: 3.06V

Battery 2

  • Cell 1: 3.08V
  • Cell 2: 3.09V
  • Cell 3: 3.00V
  • Cell 4: 2.97V

System is saying 71% state of charge. And the A-SL11 under voltage alarm is saying "battery full discharged, cell voltage below the allow to discharge cell voltage set in the app.

The manual says:

4.8.2. Cell under voltage pre-alarm thresholdWhen the cell voltage drops below this threshold, the pre-alarm signal is sent to the BMS. The purpose of the pre-alarm is to warnthe user that the system is about to shut down due to undervoltage. For more details see chapter: “System design”.The default value is 3.10 V and the range is 2.80 V to 3.15 V.

Is it correct that my system is at 71% SoC? To use the system below 70% I can just change this Cell voltage disconnect feature down to 2.80V? And are the Cell 3 and 4 readings anything to worry about?

BMV Battery MonitorLithium Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @lemonjelly,

although with Lithiums it's hard to tell SoC just from voltage, but in your case it's definitely not ok. SoC seems to be rather in the range of 10% or even lower. And it is time to charge and balance (because battery 2 seems to be slightly out of balance - see the manual for the right procedure) the batteries and stop discharging them.

There might be another issue with your battery monitor. If you have a BMV or SmartShunt as your battery monitor, what are the settings?

17 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lemonjelly avatar image lemonjelly commented ·

Hi @Stefanie,

Thanks, this is what I was worried about. Something doesn't seem to be calibrated quite right. I had the batteries set up by an electrician, who may have not realised they weren't at 100% on arrival. Tomorrow I will do a charge each battery individually, max charge current 75 A, for a 2 hour fixed absorption period, as per the manual. Then will report back.

0 Likes 0 ·
seb71 avatar image seb71 lemonjelly commented ·

You did not answer the question about how you are measuring the SOC.

Do you have a BMV or a SmartShunt?

0 Likes 0 ·
Show more comments
seb71 avatar image
seb71 answered ·

"To use the system below 70% I can just change this Cell voltage disconnect feature down to 2.80V?"

That's the "Cell under voltage pre-alarm threshold". And no, do not lower it to 2.80V. Leave it at 3.10V (or even increase it to 3.15V).

Also, leave the "Allowed-To-Discharge cell voltage" at maximum value (2.80V).


"And are the Cell 3 and 4 readings anything to worry about?"

Probably not. Cells are never exactly the same. In the case of your batteries, the cells are balanced at the top (when fully charged). There they are (or should be) equal (same voltage).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.