question

Tomasz Czernecki avatar image
Tomasz Czernecki asked

How to properly set charged voltage on BMV-712?

We have 2 x 6V 224Ah batteries in series hooked to a WFCO converter and while the converter/charger's bulk voltage is 14.4V (which it only enters after deep discharge), the absorption voltage output on this charger is only 13.6V and float is 13.2V. Meanwhile, my parallel solar charger (Victron 75/15) is set to 14.4V absorption and 13.8V float. Does this mean that the battery will only be fully charged if I have solar charging present? And if so, I'm wondering how to properly configure a BMV-712 monitor in terms of "charged" voltage - if I use 13.2V then the monitor might think the battery is full when it's not, but if I use for example 14V, the monitor may never show a full battery if I'm just charging off the converter (ie. Cloudy day / no solar).

Thank you for your help!

MPPT ControllersBMV Battery Monitormonitoringbattery system voltage
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

The main measurement the BMV (the shunt) does is "Ah in" / "Ah out" (to/from the battery).

It also knows the actual battery voltage over time.

0 Likes 0 ·
Tomasz Czernecki avatar image Tomasz Czernecki seb71 commented ·

Yes I know those things - that wasn't my question though :)

0 Likes 0 ·
seb71 avatar image seb71 Tomasz Czernecki commented ·

"but if I use for example 14V, the monitor may never show a full battery if I'm just charging off the converter (ie. Cloudy day / no solar)."


If enough Ah get into the battery, SOC will reach 100% , even if the "charged voltage" set in BMV is not reached.

0 Likes 0 ·
3 Answers
JohnC avatar image
JohnC answered ·

Hi @Tomasz Czernecki

It appears your WFCO uses different terminology than Victron. The 14.4V Victron calls 'Absorb', the 'Bulk' a transition stage on the way there. The 13.6V is 'Float', and the 13.2V 'Storage', in Victron-speak.

They'll accept charge at all those V's, but the-lower-the-slower. When the Tail Current stops (or comes close to) tailing off then your batts are full. So you set your Charged V and Tail to resync to 100% when that happens.

Your batts sound a little like GC2-pattern floodeds, and if they are let me know and I'll post up my own settings & explanation.




2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

goldspace avatar image
goldspace answered ·

I recently installed my BMV712 and had a similar question. The instructions describe that the auto synchonization of the BMV is set by "tail current". That, I believe, is the small current the batteries take temporarily after 100% charge. Tail current is an adjustable parameter in settings; BMV default tail current is 4% of capacity. Your capacity is 224 a/h; by default, a tail current of 9A for a period of time (3 min above a voltage you select) would reset the BMV to 100%. The instructions are in the manual. Refer to paragraphs 2.2 (manual, pg 10), and 4.2.1. (manual pg 21)

The other important aspect here is to determine the manufacturer's recommended float voltage. Then I suggest playing with the auto sync settings, including tail current, to find an acceptable combination of parameters in which you can be confident that you're completely charging your batteries.

Good Luck!




1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

The automatic synchronization of SOC to 100% does happen when 3 conditions are met (true). Current being under the "tail current" value set in BMV/SmartShunt is just one of them.


The conditions are:
- battery voltage must be greater than the "charged voltage" set in BMV/SmartShunt;

- current (into battery) must be smaller than the "tail current" set in BMV/SmartShunt;

- the above two conditions must be simultaneously true and must remain true for the time period set in BMV/SmartShunt.


The charging algorithm and charging voltages for various charging stages from MPPTs and grid chargers are another matter, and do not depend on the BMV/SmartShunt settings.

0 Likes 0 ·
Tomasz Czernecki avatar image
Tomasz Czernecki answered ·

Thank you all! @JohnC here is the datasheet of the battery - not sure if this is a GC2 though people have referred to it as such in some forums:

https://drive.google.com/file/d/1VWbKPs3r3bNxp0eHl0ekIga29l7vO7IE/view?usp=drivesdk

It sounds like the tail current is the more critical parameter than the charged voltage in the BMV-712. Something like a setting of ~13V should cover me for both solar and WFCO converter cases, and I'll just tweak the tail current (another user of this battery recommended 2%) for appropriate behavior. I wonder, any disadvantage to setting a really low tail current, like 1%, to ensure battery is fully charged before the BMV synchronizes? What happens if it synchronizes at a tail current of say 2% but then the battery keeps charging. Does the BMV indicate >100% charge, or will it just say 100% but not go to 99% until there is net amps lost compared to synchronization point?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

@Tomasz Czernecki

Yeh, those are close to GC2, same size but sealed and slightly different chemistry. I took the liberty of running the capacity specs through the Victron Peukert calculator. It bobbed with 1.19, so you could use that rather than the 1.25 default. (I use 1.16)

The Tail is indeed important, and it can even vary between winter and summer as batt reactivity varies. I used 0.7% in winter, but now in summer with my batts up over 30 degC and longer days, 0.5% works ok.

The Trends graph in VictronConnect is good to watch this on. This is mine today, and if you look closely you'll see a jump from 99.7% to 100% as it synched. I could set the Tail lower, but practicalities rule - I may run out of daylight on bad days.. :)

1609471499986.png

It won't go above 100%, even though the scaling suggests it might. And you must accept that 100% as a practical level, achievable in the daylight you have available, and is not a lab figure. I just accept that the 0.3% I've 'jumped the gun on' will be achieved anyway over the rest of the afternoon.

And oh, (with 48 > 12V conversion) I'm using 13.5V Float (+/- realtime temp comp) and 13.2 Charged V. Also, I found 90% Charge Efficiency best, as distinct from 89% or 91% (or the default).

Have fun tuning..


0 Likes 0 ·
1609471499986.png (47.1 KiB)
Tomasz Czernecki avatar image Tomasz Czernecki JohnC ♦ commented ·

Thanks again John - so if you keep charging beyond sync point (say, another 2 amp-hours), and then disconnect from the charger and run on battery, will the BMV not drop below 100% until you've used those 2 extra Ah beyond the sync point?

Happy new year to you and yours!

Tom

0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual