I have the following challenge:
When switching from battery operation to generator operation, the airco engine runs wild for a moment, sometimes resulting in a malfunction in the Quattro (and I am sitting stiffly upright in bed).
Situation without shore power and on battery operation:
Immediately when the generator is running AND gains access to the Quattro (via an external relay), the AC output on the Quattro supplies the voltage and frequency equal to the generator. The power will still come from the batteries! The generator will then run unloaded for a while (more voltage and higher hertz number). If after a few seconds the INTERNAL relay in the Quattro switches, it draws the power from the generator and no longer from the batteries. The drop in speed due to the load reduces the voltage and frequency. Delivery from the batteries is zero from that moment on.
How do I prevent AC out from passing through the higher frequency of the generator? Thanks in advance!