Hello,
why is the Multiplus II (ESS Mode) turning off Output 1, when I switch off the battery (Pylontech) and the Grid is NOT down?
Regards,
Ralph
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
why is the Multiplus II (ESS Mode) turning off Output 1, when I switch off the battery (Pylontech) and the Grid is NOT down?
Regards,
Ralph
Hi Ralph
It does this because ess program needs the battery to work properly.
The Multiplus is an inverter charger not an ac coupled pv inverter.
If you don't want your batteries to discharge with ess, use the gx and tell the system to keep batteries charged and it will try use solar as much as possible balanced with the grid.