I am using 700 w of solar panels into Smart solar MPPT 100/50 with a BMV 712 monitor . Can I parallel the 3 120 ah and if so is it simply neg to neg to neg and so on .
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am using 700 w of solar panels into Smart solar MPPT 100/50 with a BMV 712 monitor . Can I parallel the 3 120 ah and if so is it simply neg to neg to neg and so on .
You are on the right track. The link below is a book wiring unlimited if you check around page 18 there are some tips and diagrams to consider. It is especially important to wire the bank correctly. For current sharing for battery health.
Sometimes with a 3 battery bank you also may need to consider a bit more maintenance such as position rotation because of the current sharing issue you will run into.
Alexandra , thanks for your answer , I have read this manaul before ,, maybe blinkered by the fact it shows 4 battery not 3 . Will set it up and give a report in a week or two .
Again thanks .