Hello,
We have a Quattro 5K 120V AC, connected to our 48V DC system.
Is it possible to use a Genset with 230V AC with such inverter/charger or it needs only a 120V AC ?!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
We have a Quattro 5K 120V AC, connected to our 48V DC system.
Is it possible to use a Genset with 230V AC with such inverter/charger or it needs only a 120V AC ?!
It would be possible if you use an Autotransformer at the output of the generator.
https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf
Thanks for the feedback,
but in the Auto-transformer datasheet if is always used on the AC out, is it a common practice to use it on the AC in that case?
An autotransformer does step up or step down. It is not concerned what it is connected to. Those examples are demonstrating the various configurations that are possible to get the most out of an inverter when there are unbalanced loads.
An autotransformer will step down generator Voltage to 120V.
I don't know how your N-E (MEN) bond is arranged from the generator, so have your electrician study the datasheet and inspect your current system to ensure compatability.
WKirby, good idea
the auto transformer will work both ways
230 to 120 or 120 to 230
keep in mind that the Hz will stay the same so both the gen and the multi must be the same Hz
Thanks, of course regarding the Frequency this would be Sync between both. in this case, 60 HZ
How is your generator wired into your system? My generator is wired for both 240v and 120v per the generator manuals below:
I have the multiplus 3k connected between L0 and L1, like a split phase output of the generator. There are other loads on L1-L2 and L0-L2. Its not perfectly balanced and will have return current on L0 (neutral). Works fine. The multiplus came connected this way from the marine manufacturer.