question

markmoto avatar image
markmoto asked

SmartShunt Amps out & amps in not match ?

Hi,


Smartshunt wont show correct amps out.

When Victron AGM battery fully charged I usually have 4-6 amps left in "Consumed Ah" just before it resets to 100%

On smartshunt I adjusted Charge efficiency factor to 99% without any significant results.

What else can I do to reduce the difference please?

Using Orion Smart TR 12/12-30 to charge battery.


@markmoto

SmartShunt
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Can you make a screenshot of the settings?

0 Likes 0 ·
markmoto avatar image markmoto Matthias Lange - DE ♦ commented ·

See screen shot of smartshunt battery settings. I have increase time to 10 min so I can take screenshot before It resets to 100%. Also Orion charger set to victron default agm profile with float of 13.8

screenshot-2020-12-01-001001.jpg

0 Likes 0 ·
2 Answers
markmoto avatar image
markmoto answered ·

Hi,


I found the problem, on first install needs "Zero current calibration" even if it showing 0 in "Current".

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markmoto avatar image
markmoto answered ·

Here another screenshot of interface while battery fully charged and in float mode.

screenshot-2020-12-01-001624.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.