Hi!
I think it is possible. But only if you connect the fronius in the Multiplus Ac input. Connecting on the output Will be a problem because the Multiplus Will try to moderate the frequency on the ac output but only on the one phase of the symo. I think this is not acceptable.
If Fronius is on the Multi's input you can have this Multi only on one phase.
When grid fails only this one phase will have power.
Fronius without grid will just turn off.
Hopefully the multi controlling the fronius via modbus wont throttle down the fronius. Meaning if there is consumption on the order two phases will fronius increase power output to deliver to them as well?