I have a 150/35 solar controller connected to 3 x 144 watt solar panels. There is a discrepancy between the voltage at the batteries and the voltage taken at the solar controller. When I use the switch to cut off solar, the voltage at the controller on the battery side spikes.
Here is the situation:
House bank (2 x 210 amph lifeline 4d) will be at 12.7volts measured at the batteries while solar is on in bulk charging. At the controller, the battery terminals will measure 12.9v with a multi-meter and on the app (bluetooth). When I turn off solar using a solar cut-off switch, there is a momentary spike in voltage at the solar controller battery terminals up to 20v, then is slowly comes down to 13.8 volts. The batteries will drop to about 12.5 volts. I am not sure why the solar controller is not reading the voltage at the shunt which matches the batteries.
What is odd, is I have a BVM-712 that is reading the same voltage as the house batteries and it is sharing the same shunt? But, the BVM-712 won't read amps that the solar is putting into the batteries when it is charging. It will only measure current when I draw from the batteries. But, the controller is seeing and measuring the amps going to the battery.
I checked all the connections, tried a new fuse (250mA) going to the shunt from the positive battery terminal.