I have a problem with the two-signal BMS support in the ESS assistant.
The two-signal BMS support is described very simple and clear in this document:
https://www.victronenergy.com/upload/documents/Manual-Connecting-other-lithium-battery-systems-to-Multis-and-Quattros-EN.pdf
One signal input is used to allow charging/disable charging and the other input is used to allow discharging/disable discharging.
I selected "Disable charger" on the high-cell/battery full condition. When the BMS activates the input of the Multi, the CCGX shows "ESS #3", which means "BMS disabled charging". But the problem is, that the charger AND the inverter stop working in this case. This doesn't make sense in my opinion, because the battery is full and cannot be discharged, because the inverter is also disabled. So the system locks itself and remains in this state and cannot leave this state.
Then I switched the "Battery full"-input manually and could reproduce this behaviour as long as I wanted: The Multi is in inverter mode and discharging the battery. Then I activate the input and the inverter stops immediately. Then I deactivate the input again and the inverter starts again with discharging the battery.
When I select "Force to float" on the high-cell/battery full condition, the inverter is not affected and not disabled in this case. So this seems to work fine.
The "Battery empty"-input also works fine and only switches off the inverter, whereas the charger is not affected and still works.
I found an entry with the same problem form last year here:
https://community.victronenergy.com/questions/18191/ess-with-2-wire-bms.html
In the first answer from May 27 '19 dunno describes the same problem, which I also observe with the option "Disable charger" on the high-cell/battery full condition, but there is now answer to his question.
Can someone help of the Victron team?
Best regards
Tim


And the other bug I reported som time ago. If using ESS and your in absorption... when inverter switch to float, they discharge the excess to grid - at full power - regardless of grid setting, causing a massive flow of energy for a brief period.