question

basho33 avatar image
basho33 asked

Multiplus 24/3000 power pulse when generator switchover takes place

I have a multiplus 24/3000 and when the generator comes on (relay in the mppt) and the inverter switches from inverting to charging, i get a power surge through they system (LED lights get bright for a second) - now this pulse in power is turning off my generator. Help!

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

Try turning off the UPS selection by using VE Configure and see if this helps you. you will need a MK3 to do this adjustment if you do not have a GX device and a connection to the vrm,

There is always a small switch over when the inverter changes from gen to inverter and vice versa,

1606366294487.png


1606366294487.png (17.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.