Multiplus12v and 24v.pdf Can you connect two multiples, one 12v and one 24v as in the attached diagram?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Multiplus12v and 24v.pdf Can you connect two multiples, one 12v and one 24v as in the attached diagram?
No, it is not possible to connect the AC output of 2 different types of MultiPlus together.
For this configuration, the AC output sine wave must be synchronised, and that requires identical MultiPlus units (and additional configuration).
Hello. Can this connection scheme of two 12v and 48v multiplus inverters be applied?
Yes this should be functional, I have never done this myself but I cant see why it would not work, you would be limited to the 12 volts multiplus pass through limit
but it does not gain you much, you would be better off moving the mppt panels across to the 48 volt system ,
You may have reason for not doing the below and you may have allready considered it and it would all depend on the 1 to 1 solar rule as well
this would then allow you to run more loads during the day
just a different perspective
Hello Yes so it is limited by Multi 12v 3000W. But that's how I can make the two Lines work in series even if they are different. The first Multi of 48v is recognized by Multi 12v as the 220V mains. So many of 12 is "tricked" at the input of many 48v as if connected to the 220v network. As if you were connecting a generator to the input of the Multi 12 and it synchronizes after the generator, Multi 12V synchronizes after the multi 48v. So "I fool" Fronius that he has a network. I think that's right. Attach the diagram.