What’s the maximum capacity in AH (amp hours) battery bank can be connected to a Victron Quattro 48/15000/200 ?

MultiPlus Quattro Inverter Charger
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Jesse

There is usually more concern over minimum requirements of the bank not being met. Such as the c rating of the bank meeting the full load and possibly short term overload needs.

Maximum is usually determined by budget and charging ability, as well as the number of days of autonomous running required.

0 Likes 0 ·
Jessesolar avatar image Jessesolar Alexandra ♦ commented ·

Great. That has answered my question.

Thanks

0 Likes 0 ·
1 Answer
ossi avatar image
ossi answered ·

Hi @Jesse


As @Alexandra mentioned already your questions seems really weird, but I will answer anyhow:


65000Ah

1606307862650.png


If you walk about a big battery Bank (Lead Acid) why not use am BMV, doesnt add much to the costs compared to THIS Battery.

If you talk about a Lithium system with external BMS the Capacity you can connect is unlimited.

Please make sure that you respect leadacid MINIMUM Charging Currents of the battery supplier!!!


BR