question

curtisf avatar image
curtisf asked

Skylla IP44 equalization voltage wont go above 14.6V

I have a Skylla IP44 12/60(3) running two banks of AGM Super Cycle batteries. The battery banks are not holding a charge (voltage drops prematurely under load) and I've been advised by my Victron distributor to try equalizing the banks. The equalization voltage is set to 15.9V, but when I put the charger in manual equalization mode it won't put out any more than 14.6V. Charger state is showing as "Equalize" on my CCGX.

What am I doing wrong?

Skyllaequalisation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Saff avatar image
Saff answered ·

Hello.

What is the load level under this situation (is there any load)? If your load is more than (or close to) the output of your charger then the voltage will be held back. Are you able to try the equalisation with the banks isolated from any loads?

Cheers

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

curtisf avatar image curtisf commented ·

The load was nowhere near the charger output. One bank had 5-6 Amp load, the other had no load at all. It's a 60Amp charger.

0 Likes 0 ·
Saff avatar image Saff curtisf commented ·

What current is the charger putting in? If it's maxed out then perhaps you have a dropped cell in the bank. This could explain both the low voltage when trying equalise and also the fast voltage drop under load.