ianddindustries asked

Power assist

Hi

I have a system that requires the multiplus to have Ac out only when there is shore power (Ac in) And use the powers assist

The shore power is limited to 10 amps and the system has very short spikes of 15 amps And generally runs at around 6.5 amps so will charge the lithium battery in between spikes

Is there an assistant that can manage this or would the use of a relay be required.

Regards

Grant

powerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Paul B avatar image
Paul B answered ·

you just need to adjust the current limit in the Multiplus to 10 amps this is done with a MK3 and the victron VE configure program or you can add a Victron DMC unit which is a remote switch and Knobe

1604221720984.png


1604221720984.png (48.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ianddindustries avatar image
ianddindustries answered ·

Hi , yes but I only want the Ac out to be on when Ac in is present, so the system can’t run on the batteries, and only are only used to power assist.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Wire your loads to ACout2 ?

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @IandDIndustries

you can set the unit to 'charge only' this way it will only power up when AC is present on input.

Plus set a 10A input current limit.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ianddindustries avatar image ianddindustries commented ·

Will powerassist work on charge only

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ ianddindustries commented ·
0 Likes 0 ·
ianddindustries avatar image ianddindustries Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Hi. Just tested powerassist on charge only and it will only do passthru

Whilst on passthru the input current limit (set to 10 amps) doesn’t not work either.

0 Likes 0 ·