question

Vangelis Beligiannis avatar image
Vangelis Beligiannis asked

Does the SOC assistant condition on the Programmable relay asssistant work if the internal battery monitor of the multiplus is not enabled?

Does the SOC assistant condition on the Programmable relay asssistant work if the internal battery monitor of the multiplus is not enabled? (CCGX is present)

and further on. Does the BMV SOC value automatically overwrite the internal battery monitor value if it is selected on the CCGX?


MultiPlus Quattro Inverter Charger
2020-10-24-2.png (58.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

No, you need to activate the internal battery monitor to use the SOC as a signal.
If the BMV is selected as battery monitor in the settings of the CCGX, than the SOC from the BMV will be send to the Multi through the CCGX and the SOC of the internal battery monitor will be overwritten, but again the internal battery monitor must be activated.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vangelis Beligiannis avatar image Vangelis Beligiannis commented ·

Thank you !!!!!!!!!!!!!!!

0 Likes 0 ·