Discrepancies in battery voltage between MPPT and BMV

Our MPPT often shows a different voltage reading to what the battery actually is. (13.5 vs 13.3). This means that our solar goes into absorption/float before the battery is actually full. Any ideas why? I have set up a smart network which helps but we still need to know where the error is.

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
klim8skeptic avatar image
klim8skeptic answered ·

There is no Smart Network symbol on the mppt screen.

Join the MPPT to the BMVs VE.Smart network.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

emmakrieg avatar image emmakrieg commented ·

I turned it off to get the screenshots and to show how they are differnet

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ emmakrieg commented ·

Once they are connected together via the VE.Smart network, the MPPT will use the more accurate battery voltage provided by the BMV/SmartShunt.

There is no error, voltage rise/drop is a physical property of electrical systems. Increasing wire size, reducing length of cable run, reducing current, reducing the number of connection points will all reduce the amount of voltage differential.

But the easiest solution is to use the calibrated readings of the BMV, via the correctly configured VE.Smart network, so the MPPT will accurately charge the battery.

0 Likes 0 ·
emmakrieg avatar image emmakrieg Guy Stewart (Victron Community Manager) ♦♦ commented ·

The battery voltage as shown on MPPT fluctuates rapidly (every second). Never seems to be steady like the voltage reading on BMV. Is this normal? The smart network helps it but it stills goes into absorption too early (before full)

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ emmakrieg commented ·

That sounds like it could be a bad connection, or partially blown fuse.

If you have a multimeter, test voltage at every connection between the battery terminal lugs and the MPPT battery connection screws to see if you can find where it varies.

0 Likes 0 ·