we have a system composed by two victron mppt charger working in parallel not syncronized as per victron datasheet . in this case the charging phase of the two charger will be not the same.it is safe for the battery?what do you suggest?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
we have a system composed by two victron mppt charger working in parallel not syncronized as per victron datasheet . in this case the charging phase of the two charger will be not the same.it is safe for the battery?what do you suggest?
By synchronized, are you expecting that the chargers go 50/50 on the charging load?
Are they connected to each other in some way to enable communication?
I have not had a problem with overcharging or undercharging, if that is what you are asking
The system will not work optimally in this way. what will happen is you can end up with one unit on bulk and the other on absorbtion or float as they detect the voltage. This could end up with the batteries either taking longer to reach 100% soc of charge or them never reaching 100 soc. By syncronising you ensure the charges are at the same stage there by optimising the charging.
since they woptking in parallel and connect to a battery sytem,they should detect the same voltage,the battery..or not?
Hi @corpa
What kind of batteries are you using, and what problems are you experiencing?