question

dgmar-ni avatar image
dgmar-ni asked

Setting up an AC coupled system with string inverter Aurora 6 kW with Multiplus or Quattro

Hi,

I have a customer which already has a grid tied system using 27 modules of 230W and 1 string inverter 6 kW Aurora model PVI-6000-OUTD-US.

I understand that CCGX has built in a FRONIUS module for AC coupled systems and I have the doubt for other models that can be compatible and if there is an specific software product from Victron to do it.

Regards.

MultiPlus Quattro Inverter Chargerac coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hello,

It is not limited to Fronius, though that provides the best supported experience.

Please read these two documents about the do's and don'ts of AC coupled solar with Victron systems:

https://www.victronenergy.com/live/ac_coupling:start

https://www.victronenergy.com/live/assistants:pv-inverter-support

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phil Gavin avatar image
Phil Gavin answered ·

For clarity, is your question whether the Venus software can be used for an ABB inverter in the absence of a Multi?

Or do you intend to introduce a Multi in combination with it?


5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phil Gavin avatar image Phil Gavin commented ·

If it is the latter:

This isn't an official answer, but relies on personal WWW research.

The latest ABB inverters have very recently been integrated into Venus software, including the Zero feed-in capability. ( Note* This is on a trial basis, it only applies to ABB's latest generation of models and continued support is not implied).

The capability of frequency-shifting power control existed in the earlier models ( at least since VDE 4105 certification), and still exists in the later models. ( FSPC is a degree of control allowing AC coupling, but without the Zero feed-in capability).


1 Like 1 ·
dgmar-ni avatar image dgmar-ni Phil Gavin commented ·

Thank you Phil for your feedback. Yes is the last option you mentioned that customer wants to integrate a Multi or Quattro on the existing system with the ABB inverter. I'll search on ABB's website for more information.

0 Likes 0 ·