How much Wp from solar panels can I use in the MP II?

I am planning to install 18 panels of 450Wp (Voc 49,7V Isc 11,32A), 9 connected to each MPPT 250/100 with 3S3P giving me these values: 149,1V 33,96A.


I was reading the datasheet for the MP II48/5000/70-50 https://www.victronenergy.com/upload/documents/Datasheet-MultiPlus-II-inverter-charger-EN.pdf and it says maximum 50A for Maximum AC input current.

I am not sure if I could use this MPII using 2 MPPT's at that Amps. Can anyone give me a hint on this issue? Thank you

Multiplus-IIMPPT ControllersSolar Panel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@tpwchr

The 50A refers to AC charging or mains charging. Mppts are dc chargers so there is not really a limit.

In a good ess system the mppts will assist with loads as well as charge the battery from solar.

So it sounds like you have a good balance for charging and running heavy loads.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tpwchr avatar image tpwchr commented ·

Alright, it is meant to be used in an off-grid system, but im glad its a good balance. thanks!

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ tpwchr commented ·

Have you played with the online mppt calculator?

https://www.google.com/url?q=https://www.victronenergy.com/mppt-calculator&sa=U&ved=2ahUKEwjVlv__sJbsAhW7ShUIHRAxAh8QFjAAegQIDRAB&usg=AOvVaw3KnrgQeacGZAZ-82ePnoq-

You can check your yeilds over the year and see where you may be using your back up generator the most during the year by setting your location as well.

0 Likes 0 ·