I note many have had a similar problem, but all the "remedies offered tried with no improvement"
System is 24V with CCGX , Multiplus 5000VA/24 2 x MPPT Solar chargers, BMV, 12 x OPzV600 Cells, previously connected offgrid, but now with Grid connection,
System updated to latest firmware on all components, and configure with ESS,
Sorry to be a bore with the following but most replies ask for full tech setups to help, !!
Battery capacity set to 600AH, Battery monitor enabled and with SOC Bulk Finished 85%, charge efficiency 0.80
Inverter Output V = 230, DC inputs 21, 24, 22 volts respectively
AES Enabled, (Default)
Charger
Enabled
Charge Curve Adaptive+ Battery safe
Absorb 29.6
Float 26,4
Charge Current 50A,
repeat Absorb 8 hr
ditto interval 7 days
max absorb time 8 hours
Temp comp -32.4
Virtual switch , = Do not use
Assistant ESS ( Energy storage system) with
1 Battery System set to Use OPzS or OPzV batteries
Battery capacity 600AH
Sustain during 24Hours 23.00V
After 24 hours 25.00V
Dynamic Cut off in order, 24,00 V ,, 22,50V ,, 21,10V ,, 20,00V
restart offset 0.60V
No PV inverters
VE Config,
Battery Cap 600AH
Powerassist unchecked
Lithium batteries Unchecked
Dynamic current Limter unchecked
Storage Mode Unchecked,
On CCGX the following has been set under the ESS and DVCC setting
DVCC currently off ( Disabled)
ESS
Mode Optimised ( without battery life)
Grid Metering Inverter/Charger
MIN SOC ( Unless grid fails) 70%
Limit charge power disabled
Limit inverter power disables
Grid Set Point 50W
Grid Feed in enabled ( DC coupled PV - Feed in Excess)
Feed-in limiting active, NO
The comms is provided by the VE direct
your thoughts would be greatly appreciated,