Positive x Earth voltage low on test

Victron phoenix 12/800 inverter installed on a steel Hull boat

When I test across live and negative I get 220v. When I test live to earth I'm getting 140v and when a load is applied I'm getting 80v.


I have replace the inverter and get the same issue. I have run a negative cable to the Hull and the problem persists. The appliance I want to run requires a good earth to run properly.


Any ideas. Help much appreciated.

voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

These models are shipped with the AC output isolated from the chassis.
You need to follow the instructions in the manual, see Appendix A on page 12 of the manual linked below:

https://www.victronenergy.com/upload/documents/Manual-Phoenix-Inverter-VE.Direct-250VA-1200VA-EN-NL-FR-DE-ES-IT.pdf