question

Martin Gasthuber avatar image
Martin Gasthuber asked

unexpected Inverter shutdown

Hi,

after running several months with no issue at all, the MP II swicthed off and no message appeared on the GX not the VRM alarm log. Later i discovered irregular behaiviour of the SOC coming from the BYD BMS (a call to EFT is already opened) - nevertheless, i would expect some sort of logging from the MultiPlus II about that - any other location/source i could look at ? The only change within the last 2 weeks was updating the GX to 2.60.

best regards,

Martin

Multiplus-IIBYD
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@martghh

Is this still an issue?

The BYD may not have reported an issue to the gx at all. Is there a way to interface with the BYD at all maybe find out if there was a weak cell and the battery shut down?

The other thing to check is if the multi's own battery monitor is checked and configured. I have had systems when the multi has noticed an issue on ve bus voltage but the batteries say nothing yet have a weak cell and shut it off obviously dropping the voltage of the system and causing a shutdown.

0 Likes 0 ·
Show more comments